A chiller's purge unit is discharging normally on every cycle, yet the condenser pressure keeps climbing through the afternoon. What does that combination point to?

Correct Answer

A) Air is coming in faster than the purge can remove it, so the leak needs to be found now

A purge that is cycling and actually discharging is working. If non-condensable gas is still accumulating fast enough to drive the head up, the machine is taking air in faster than the purge can pull it out. That is a large leak, and the response is to find it rather than to rebuild the purge. A failed purge looks different: it runs without discharging, and the pressure climbs with nothing leaving the exhaust.

Answer Options
A
Air is coming in faster than the purge can remove it, so the leak needs to be found now
B
The purge compressor has failed, so nothing is being removed from the top of the condenser
C
The condenser water flow has been lost, so the machine is condensing at a higher temperature
D
The refrigerant charge is high, so the extra liquid is backing up and flooding the condenser

Why This Is the Correct Answer

Purge capacity is finite, measured in ounces of gas per cycle. When the in-leakage rate exceeds it, the condenser accumulates non-condensable gas even though the purge is functioning correctly, and head pressure rises. The distinguishing evidence is that the purge is discharging: the device is doing its job and the machine is simply drinking faster than it can drink.

Why the Other Options Are Wrong

Option B: The purge compressor has failed, so nothing is being removed from the top of the condenser

A failed purge would not be discharging. The fact that gas is leaving the exhaust on every cycle is what rules the purge itself out.

Option C: The condenser water flow has been lost, so the machine is condensing at a higher temperature

Lost condenser water flow raises head pressure too, but it would show as a rise in leaving water temperature and would not drive continuous purge cycling.

Option D: The refrigerant charge is high, so the extra liquid is backing up and flooding the condenser

Overcharge can raise head pressure on some machines, but it does not generate non-condensable gas or keep a purge cycling and discharging.

Memory Technique

Listen at the exhaust. Something coming out blames the machine; nothing coming out blames the purge.

Reference Hint

A functioning purge that cannot hold condenser pressure down indicates an air leak larger than the purge unit's capacity.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.