A chiller cannot be taken out of service yet, and the technician wants to narrow down where air is being drawn in while the machine keeps running. Which instrument can do that?

Correct Answer

A) An ultrasonic detector, which picks up the high frequency sound of air rushing through the opening

Air forced through a small opening by a pressure difference makes noise well above the range of human hearing, and an ultrasonic detector converts that to something an operator can hear in headphones. It works in exactly the situation where every refrigerant-sensing instrument fails, because on the vacuum side nothing is coming out to sense. It narrows the search to a flange or a seal so the crew knows where to concentrate when the machine finally comes down.

Answer Options
A
An ultrasonic detector, which picks up the high frequency sound of air rushing through the opening
B
A halide torch, which changes flame color when refrigerant vapor is drawn across the reaction plate
C
An electronic halogen detector, which alarms when refrigerant is drawn past its sensing element
D
An infrared refrigerant analyzer, which reads the refrigerant content of the air near the opening

Why This Is the Correct Answer

Ultrasonic detection listens for turbulence rather than sniffing for refrigerant, so the direction of flow does not matter. On a running low-pressure machine the leak is drawing air in, which produces the same high frequency signature as gas escaping. It is the one detection method that works before the charge has been recovered and the shell pressurized.

Why the Other Options Are Wrong

Option B: A halide torch, which changes flame color when refrigerant vapor is drawn across the reaction plate

A halide torch responds to refrigerant reaching the flame, and on the vacuum side no refrigerant is coming out. An open flame near a chiller also risks producing toxic decomposition products.

Option C: An electronic halogen detector, which alarms when refrigerant is drawn past its sensing element

An electronic halogen detector needs refrigerant to escape past its tip. On a section under vacuum there is nothing for it to draw in.

Option D: An infrared refrigerant analyzer, which reads the refrigerant content of the air near the opening

An infrared analyzer is still a refrigerant sensor. It measures what is in the air around the machine, and a vacuum leak puts nothing there.

Memory Technique

Under vacuum you cannot smell the leak, but you can hear it.

Reference Hint

A leak drawing air into a machine under vacuum can be located by ultrasonic detection, because refrigerant sensing instruments need refrigerant to escape.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.