EstatePass
epa-608-type-2Safety & Service Practicemedium

A refrigerant cylinder is connected to the high side of a system for liquid charging and the compressor is then started with the cylinder valve still open. What is the danger in that arrangement?

Correct Answer

C) Discharge pressure can push back into the cylinder and overfill it

Once the compressor runs, the high side climbs above the pressure in the cylinder, and the cylinder becomes the low point in that path. Refrigerant then flows the wrong way, back into a container that already holds a charge, and a cylinder pushed past its fill limit and warmed by discharge gas is a rupture risk. Liquid charging into the high side is done with the compressor off, and the cylinder is closed and disconnected before it is started.

Answer Options
A
The cylinder will empty into the system faster than the metering device allows
B
The refrigerant will fractionate as it passes backward through the hose
C
Discharge pressure can push back into the cylinder and overfill it
D
The liquid line will collapse under the vacuum the compressor creates

Why This Is the Correct Answer

With the compressor running, discharge pressure exceeds cylinder pressure, so the flow reverses and refrigerant is pushed back into the cylinder. A cylinder taking a return flow can pass its fill limit without the technician noticing, and it is being warmed at the same time. Liquid charging on the high side is therefore done with the system off, and the cylinder valve is closed before startup.

Why the Other Options Are Wrong

Option A: The cylinder will empty into the system faster than the metering device allows

Charging faster than a metering device would pass is exactly why high side liquid charging is done with the compressor off. The reverse flow is the hazard once it runs.

Option B: The refrigerant will fractionate as it passes backward through the hose

Fractionation happens when vapor is drawn off a blend. Liquid moving through a hose in either direction does not separate the components.

Option D: The liquid line will collapse under the vacuum the compressor creates

Refrigerant tubing does not collapse under any pressure a compressor develops. The pressure difference here drives flow, it does not crush the line.

Memory Technique

Start the compressor and the high side becomes uphill. Your cylinder is now at the bottom of the hill.

Reference Hint

Charge liquid into the high side only with the compressor off, and close the cylinder valve before startup.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.