A technician runs a small flow of dry nitrogen through the tubing while brazing new line set into a refrigeration system. What does that flow accomplish?

Correct Answer

B) It keeps oxygen away from the hot copper so black oxide scale does not form inside the tubing

Copper heated in air grows a layer of black oxide on the inside surface. That scale flakes off as the system runs and travels with the oil until it lodges in a filter drier, a screen or a metering device, and it also contaminates the joint area. A slow flow of dry nitrogen displaces the oxygen inside the tube so the scale never forms. The flow has to be small and there must be an open path out of the tubing, so the gas moves through rather than building pressure behind the joint.

Answer Options
A
It cools the joint so the filler metal sets up faster after the torch is pulled away from the copper
B
It keeps oxygen away from the hot copper so black oxide scale does not form inside the tubing
C
It raises pressure inside the tubing so the filler metal is pushed into the joint gap
D
It tests the joint for leaks at the same moment the joint is being made and heated

Why This Is the Correct Answer

Oxide scale requires oxygen and heat. Removing the oxygen from inside the tube by displacing it with an inert gas prevents the reaction entirely, which keeps the inside of the new tubing clean and keeps loose scale out of the system's metering devices and screens.

Why the Other Options Are Wrong

Option A: It cools the joint so the filler metal sets up faster after the torch is pulled away from the copper

The flow is far too small to cool anything, and quick cooling of a brazed joint is undesirable in any case. The nitrogen is there to keep air off the inside of the copper.

Option C: It raises pressure inside the tubing so the filler metal is pushed into the joint gap

Filler metal is drawn into a properly heated, properly fitted gap by capillary action. Pressure behind the joint would blow molten filler back out of it rather than pushing it in.

Option D: It tests the joint for leaks at the same moment the joint is being made and heated

Leak testing is a separate step, done after the joint is complete and cool, with the system brought to a controlled test pressure. A purge flow tells the technician nothing about tightness.

Memory Technique

Flow it, do not blow it. The nitrogen is there to chase out the oxygen, not to push on anything.

Reference Hint

Flowing dry nitrogen through tubing during brazing prevents internal cupric oxide scale formation. An open vent path is required.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.