EstatePass
epa-608-type-2High-Pressure Appliance Scopehard

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

Correct Answer

D) As a small appliance, since it is factory sealed and holds under five pounds

The water loop carries water, not refrigerant, so the piping the installer runs is not part of any refrigerant circuit. Each heat pump has its own sealed refrigerant circuit that left the factory assembled, charged and hermetically sealed, holding four pounds. That is the small appliance description in full, so each unit is a small appliance regardless of how many of them share a building or a loop.

Answer Options
A
As part of a single high-pressure appliance made up of the whole loop
B
As a high-pressure appliance, because the water loop is field piped
C
As a very high-pressure appliance, because of its operating pressures
D
As a small appliance, since it is factory sealed and holds under five pounds

Why This Is the Correct Answer

The small appliance definition asks three things: the unit was fully manufactured, charged and hermetically sealed at the factory, and it normally holds five pounds or less. Each of these heat pumps meets all three. The field piping carries loop water and never touches the refrigerant circuit, so it does not make the unit field assembled and does not join the units into one appliance.

Why the Other Options Are Wrong

Option A: As part of a single high-pressure appliance made up of the whole loop

Refrigerant cannot pass from one heat pump to another through the water loop, so the units are not one appliance. Each sealed circuit stands alone.

Option B: As a high-pressure appliance, because the water loop is field piped

The field piping on this system carries water. Piping that never contains refrigerant has no effect on how the refrigerant circuit is classified.

Option C: As a very high-pressure appliance, because of its operating pressures

Very high-pressure describes refrigerants that boil far below the ordinary range. It is not a label for equipment that runs at elevated operating pressures.

Memory Technique

Follow the refrigerant, not the pipefitter. If the installer's pipe holds water, the unit is still factory sealed.

Reference Hint

Small appliance: factory manufactured, charged and hermetically sealed, normally holding five pounds or less of refrigerant.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

An older chiller is charged with R-114, a refrigerant that boils just below forty degrees Fahrenheit at atmospheric pressure. Which class does the regulation place that appliance in?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.