A technician opens the electrical panel of a rooftop unit after pulling and locking out the disconnect at the curb. What inside that panel still has to be treated as live?
Correct Answer
C) The run and start capacitors, which can hold a dangerous charge after power is removed
Locking out the disconnect removes the incoming supply but does not empty the capacitors. A run or start capacitor can hold enough stored energy to injure or kill after the power is gone, and start capacitors on larger equipment are particularly dangerous. Capacitors must be discharged through an appropriate resistor before terminals are touched, and the absence of voltage should be verified with a meter that has been proven on a known live source. There is also often a second power source feeding controls from a separate circuit.
Why This Is the Correct Answer
Capacitors store energy by design and hold it after the supply is removed. That stored charge is available at the terminals whether or not the disconnect is locked out, so it has to be deliberately discharged and then verified as absent before any work begins.
Why the Other Options Are Wrong
Option A: The low-voltage thermostat wiring, which carries line voltage whenever the disconnect is open
Thermostat wiring runs at low voltage and it does not become energized because the disconnect was opened. That description reverses how the circuit works.
Option B: The compressor terminals, which stay energized by the crankcase heater circuit
A crankcase heater is fed from the same supply that the disconnect removes, and it does not energize compressor terminals for service purposes.
Option D: The contactor coil, which remains energized until the unit finishes cooling down
A contactor coil is de-energized when its supply is removed. It has no stored energy and does not stay hot while equipment cools.
Memory Technique
The lock stops the power coming in. It does nothing about the power already parked in the capacitor.
Reference Hint
Locking out the disconnect removes supply voltage only; capacitors retain stored charge and must be discharged and verified before contact.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
The low stage of a cascade system is charged with R-13, a very high-pressure refrigerant, and the charge is under fifty pounds. What evacuation level does the table set for a very high-pressure appliance?
Next Question
A technician is about to set the regulator for a dry nitrogen leak test on a split system that includes an accumulator and a receiver. What determines how high that test pressure may be set?