epa-608-type-2Recovery & Evacuationmedium

After the required evacuation level has been reached and the repair is finished, many technicians keep pulling the system down to a few hundred microns before charging. What is the standing of that deeper vacuum?

Correct Answer

A) It is a service practice aimed at removing moisture and air before charging

The evacuation levels in the regulation govern one thing: how far the appliance must be brought down before it is opened, so that refrigerant does not escape. Nothing in them concerns the quality of the vacuum before recharging. Pulling to a few hundred microns after the repair is an industry practice, taught because moisture boils off very slowly and because air left in the system raises head pressure and forms acid with the oil. It protects the equipment rather than satisfying a rule.

Answer Options
A
It is a service practice aimed at removing moisture and air before charging
B
It is the level the regulation sets before an appliance may be opened
C
It is required whenever the recovery machine was built after November 1993
D
It is required only on appliances holding two hundred pounds or more

Why This Is the Correct Answer

The regulation's evacuation levels apply before the appliance is opened and are written in inches of mercury vacuum. The deep vacuum pulled afterward, usually measured in microns, is a workmanship standard that exists to boil off moisture and clear non-condensables so the system runs at design pressures and the oil does not turn acidic. Reaching it is good practice and is often required by the equipment manufacturer, but it is a different target with a different purpose.

Why the Other Options Are Wrong

Option B: It is the level the regulation sets before an appliance may be opened

The level required before opening an appliance is stated in inches of mercury vacuum and is far shallower than a few hundred microns on every high-pressure row.

Option C: It is required whenever the recovery machine was built after November 1993

The November 1993 split changes the required evacuation level before opening. It has nothing to do with how deep a system is dried before recharging.

Option D: It is required only on appliances holding two hundred pounds or more

Charge size selects a row of the evacuation table. It does not create a dehydration requirement for large appliances and exempt small ones.

Memory Technique

Inches before you cut, microns before you charge. Two numbers, two jobs, one pump.

Reference Hint

Evacuation levels in inches of mercury govern opening an appliance; deep micron vacuums before charging are service practice.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.