Rather than one very long single pull, a technician evacuates a contaminated system three times and breaks the vacuum with dry nitrogen between the pulls. Why does that approach clean the system more thoroughly?

Correct Answer

C) Each nitrogen sweep mixes with and carries away moisture and non-condensables, so the following pull starts from a cleaner system

A single long pull leaves you waiting for the last stubborn moisture to boil off on its own. Breaking the vacuum with dry nitrogen does two useful things: it raises the pressure so trapped moisture in oil and in dead-end passages can move, and the dry gas mixes with the water vapor and contaminants so the next pull carries them out together. Repeating the cycle reduces what remains by a fraction each time, so three moderate pulls with sweeps beat one very long pull on a wet or contaminated system.

Answer Options
A
Each nitrogen charge chemically neutralizes the acid that the burnout left behind in the oil and the tubing
B
The nitrogen raises system pressure enough to push the moisture out through the open service valves between one pull and the next one
C
Each nitrogen sweep mixes with and carries away moisture and non-condensables, so the following pull starts from a cleaner system
D
Breaking the vacuum lets the pump cool between pulls, so each new pull reaches a deeper vacuum than the last

Why This Is the Correct Answer

The sweep gas acts as a carrier. Dry nitrogen entering a system under vacuum dilutes whatever water vapor and non-condensables are present and reaches passages the pump alone drains slowly. Each pull then removes that mixture, so the residual contamination falls by a multiple with every cycle rather than crawling down a plateau.

Why the Other Options Are Wrong

Option A: Each nitrogen charge chemically neutralizes the acid that the burnout left behind in the oil and the tubing

Nitrogen is chemically inert and neutralizes nothing. Acid from a burnout is dealt with by removing the contaminated oil and refrigerant and by installing the appropriate filter driers, not by a gas charge.

Option B: The nitrogen raises system pressure enough to push the moisture out through the open service valves between one pull and the next one

The nitrogen is not blown out through the valves in this procedure; it is drawn out by the next evacuation. Purging a system that still held refrigerant out through open valves would also be a release.

Option D: Breaking the vacuum lets the pump cool between pulls, so each new pull reaches a deeper vacuum than the last

Pump temperature is not what limits the pull here, and a pump does not reach deeper simply for having rested. What improves between pulls is the state of the system, not the state of the pump.

Memory Technique

Nitrogen is a broom, not a chemical. Sweep, pull, sweep, pull.

Reference Hint

40 CFR 82.156 sets evacuation requirements. Triple evacuation with dry nitrogen sweeps is accepted industry practice for wet or contaminated systems.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.