Under the ordinary slope rule in 2025 CPC 708.1, a 3-inch horizontal building drain is laid at 1/4 inch fall per foot. What fall is needed over a 64-foot horizontal run?
Correct Answer
D) 16 inches total.
2025 CPC 708.1 sets the ordinary minimum slope at 1/4 inch per foot. For this 3-inch drain, 64 × 1/4 = 16 inches of fall. The reduced-slope exception concerns building drains at least 4 inches in diameter under specified impracticality conditions and prior approval. Source: https://epubs.iapmo.org/2025/CPC/
Why This Is the Correct Answer
2025 CPC 708.1 sets the ordinary minimum slope at 1/4 inch per foot. For this 3-inch drain, 64 × 1/4 = 16 inches of fall. The reduced-slope exception concerns building drains at least 4 inches in diameter under specified impracticality conditions and prior approval. Source: https://epubs.iapmo.org/2025/CPC/
Independent practice; verify any reference hint against the edition and category permitted for your booking. Official exam and reference-list sources →
More Class B Trade Questions
An attic furnace platform blocks required access to service panels. What should be maintained?
A panel edge called out for blocking in the structural notes is left unsupported. What should be installed?
A new dwelling laundry area has a 125-volt, 20-ampere receptacle supplied by a 120-volt single-phase circuit, without required personnel ground-fault interruption. Which protection is missing?
Which listed hazard is directly increased by carrying a forklift load high while traveling through a doorway?
A penetration through a rated gypsum wall is patched with ordinary joint compound only. What must be maintained?
A shear wall panel is installed but the specified edge nailing is missing at panel edges. What is the issue?
A service panel is installed where stored material blocks the working area. What must be maintained?
A fire-rated wall patch is finished with standard materials without matching the tested assembly. What must be preserved?
A joist hanger is installed with drywall screws instead of the fasteners specified by the hardware manufacturer. What should be corrected?
A field change includes 28 added labor-hours at $69 per hour plus $880 in material. What direct cost should be priced before markup?