A 50-ampere, 120/240-volt branch circuit is supplying a vending machine. What is the minimum size of the overcurrent protection required for this circuit?

Texas Master exam practice question · Branch Circuits

A 50-ampere, 120/240-volt branch circuit is supplying a vending machine. What is the minimum size of the overcurrent protection required for this circuit?

  • A25-ampere
  • 50-ampere
  • C75-ampere
  • D100-ampere

Exam tip

Ensure you understand the requirements for overcurrent protection based on the type of load.

Why B is correct

According to 210.11(B), the overcurrent protection for a vending machine must be not less than the rating of the branch circuit. Therefore, the minimum size of the overcurrent protection required is 50 amperes.