A 20-ampere, 120/240-volt branch circuit is supplying a kitchen range. What is the minimum size of the overcurrent protection required for this circuit?
- A15-ampere
- B20-ampere
- 30-ampere
- D40-ampere
Exam tip
Always refer to the specific requirements for overcurrent protection for kitchen ranges.
Why C is correct
According to 210.11(A), the overcurrent protection for a kitchen range must be not less than 30 amperes. The 20-ampere and 15-ampere options are insufficient, and the 40-ampere option is not required.