EstatePass

A balanced 480-volt three-phase load draws 35 amperes at 0.85 power factor. Using 1.732, approximately how much real power does it use?

Texas Journeyman exam practice question · Calculations & Theory

A balanced 480-volt three-phase load draws 35 amperes at 0.85 power factor. Using 1.732, approximately how much real power does it use?

  • 24.7 kW
  • B14.3 kW
  • C20.2 kW
  • D29.1 kW

Why A is correct

Three-phase real power is 1.732 × voltage × current × power factor. The calculation is 1.732 × 480 × 35 × 0.85 = 24,731 watts, or approximately 24.7 kW.

Practice 4 more Calculations & Theory questions

Timed mock exams, a wrong book and flashcards — one subscription covers every contractor exam line.

Start studying free