1. The approved plans show a fire-resistance-rated assembly on that wall, and the builder asks whether he can substitute a lighter assembly to save on labor. Under the IRC, what governs the required separation between the two dwelling units?
- AA two-hour rated assembly is required wherever a wall separates dwelling units, the rating the code assigns to townhouse common walls
Two hours is the separation assigned to townhouse common walls, not to the units of a two-family dwelling. Carrying that number across is the classic townhouse and duplex mix-up, and it over-rates the assembly.
- A one-hour rated assembly is required, and a half-hour assembly is permitted only where an approved automatic sprinkler system is installed
- CNo rating is required so long as the wall is framed as two independent stud walls with a continuous air space separating them
Double stud framing with an air space is a sound control detail, not a rated assembly. Fire resistance comes from a tested assembly, and no amount of framing separation substitutes for the rating the code requires.
- DA rating is required on the floor-ceiling assembly only, because the vertical separation between units in a two-family dwelling is unregulated
The code requires the rating on both the walls and the floor-ceiling assemblies separating dwelling units. Rating only the horizontal separation leaves fire free to travel from unit to unit through the wall.
Why B is correct
The baseline separation between dwelling units in a two-family dwelling is a one-hour fire-resistance-rated assembly, applied to walls, floors or both as the geometry requires. The only relief the code offers is a reduction to a half-hour rating where an approved automatic sprinkler system is installed throughout the building. Nothing in the section lets a builder trade the rating away for a heavier framing arrangement.
What this question is testing
The item tests whether the candidate knows the baseline separation for a two-family dwelling, knows the single condition that permits a reduction, and understands that a fire-resistance rating comes from a tested assembly rather than from framing geometry.
On the job
Duplexes get built by small builders who also build single-family houses, and the rated wall is the detail most often treated as ordinary framing. The giveaways at inspection are single-layer board where the listing calls for two layers, the wrong screw spacing, and penetrations for outlets and plumbing cut back to back through the assembly. Ask which tested assembly the wall is built to and check the actual construction against that listing rather than against a general impression of what a rated wall looks like.
Memory technique
One hour dry, half an hour wet. Sprinklers buy you back half the rating.
Exam tip
One hour is the baseline between units, and sprinklers are the only path to a half hour.
Where to look it up
IRC Chapter 3, Section R302.3 for two-family dwellings, with R302.2 covering townhouses separately.