For a mat foundation on soft clay with bearing capacity of 2,000 psf, what is the maximum building load if the foundation is 40 ft × 60 ft?

Correct Answer

A) 4,800 kips

Maximum load = bearing capacity × area = 2,000 psf × (40 ft × 60 ft) = 2,000 × 2,400 = 4,800,000 lbs = 4,800 kips.

Answer Options
A
4,800 kips
B
6,000 kips
C
3,200 kips
D
7,200 kips

Why This Is the Correct Answer

Maximum allowable load = allowable bearing pressure × foundation area. Area = 40 ft × 60 ft = 2,400 sq ft. Load = 2,000 psf × 2,400 sq ft = 4,800,000 lbs. Converting: 4,800,000 lbs ÷ 1,000 = 4,800 kips. This is a direct application of the bearing capacity formula with no partial safety factors or other adjustments needed because the problem provides the allowable (design) bearing capacity directly.

Why the Other Options Are Wrong

Option B: 6,000 kips

6,000 kips would result from using a bearing capacity of 2,500 psf (2,500 × 2,400 = 6,000,000 lbs = 6,000 kips) — a 25% overestimate. This is not the value given, and using it would allow a load that exceeds the safe capacity, risking foundation settlement or failure.

Option C: 3,200 kips

3,200 kips corresponds to approximately 1,333 psf bearing capacity with the 2,400 sq ft area, or alternatively using only part of the foundation area. This result does not match any logical rounding of the given values and represents an arithmetic error.

Option D: 7,200 kips

7,200 kips would require 3,000 psf bearing capacity (3,000 × 2,400 = 7,200,000 lbs = 7,200 kips). Using 3,000 psf when the problem states 2,000 psf is a 50% overestimation error, which would significantly underdesign the foundation.

Memory Technique

The formula is simple: P_max = q_allow × A. Always do it in three steps: (1) Calculate area in sq ft, (2) Multiply by bearing capacity in psf to get pounds, (3) Divide by 1,000 to convert to kips. Write it as: '2,000 × 2,400 = 4,800,000 lb = 4,800 kips.' The clean numbers make this calculation exam-friendly.

Was this explanation helpful?

More California Questions

A contractor is installing shear walls in a residence located in Seismic Design Category D. The engineer's plans call for 15/32-inch structural sheathing with 8d nails at 6 inches on center at panel edges. The contractor wants to substitute 7/16-inch OSB with the same nailing. Is this substitution acceptable?

You are reviewing plans for a mixed-use building where the ground floor will house a restaurant with commercial kitchen equipment. The architect has specified standard residential electrical requirements throughout. What Title 24 compliance issue should you identify?

According to CBC seismic provisions, what is the concept behind the 'strong column, weak beam' design philosophy?

A residence in California has 2,800 sq ft of conditioned space. The HVAC system efficiency is 16 SEER. What is the approximate Title 24 compliance margin compared to the minimum 14 SEER requirement?

You're constructing a foundation on liquefiable soils identified in a California coastal area. The geotechnical report recommends deep foundations. Which option is most commonly specified?

A contractor is installing a heat recovery ventilation (HRV) system to comply with Title 24. The system serves a 2,000 sq ft house with 3 bedrooms. What is the minimum required ventilation rate?

During construction of a basement in sandy soil conditions, you encounter groundwater at 4 feet below grade. The basement extends 8 feet below grade. What is the critical design consideration per CBC?

During a seismic retrofit project, you discover that existing concrete has a compressive strength of 2,200 psi. The engineer specifies new anchor bolts that require 2,500 psi minimum concrete strength. What is the most appropriate action?

What is the maximum allowable notch depth in a 2x10 floor joist per CBC requirements?

You're reviewing plans for a wood-framed structure in seismic design category D. The project calls for a shear wall with 15/32-inch structural sheathing and 8d nails spaced 6 inches on center at panel edges. What is the allowable shear value per the CBC?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.