A contractor is building a single-family residence with 2x10 floor joists spaced 16 inches on center spanning 14 feet. The building is located in Seismic Design Category D. What is the maximum allowable deflection under live load according to CBC?

Correct Answer

B) L/240 = 0.70 inches

For floor joists in residential construction, CBC allows deflection of L/240 under live load. With a 14-foot span (168 inches), the maximum deflection is 168/240 = 0.70 inches.

Answer Options
A
L/360 = 0.47 inches
B
L/240 = 0.70 inches
C
L/300 = 0.56 inches
D
L/180 = 0.93 inches

Why This Is the Correct Answer

CBC Table 1604.3 specifies deflection limits for floor members under live load as L/240, where L is the span length. With a 14-foot span (168 inches), the maximum allowable live-load deflection is 168 ÷ 240 = 0.70 inches. The Seismic Design Category D designation is contextual background and does not change the deflection limit for floor joists under live load.

Why the Other Options Are Wrong

Option A: L/360 = 0.47 inches

L/360 (0.47 inches) is the deflection limit for floor members supporting plaster or brittle finishes, or for roof members under live load. It is more restrictive than required for a standard wood floor joist under live load. Applying L/360 to this scenario is overly conservative and reflects confusion between floor and brittle-finish criteria.

Option C: L/300 = 0.56 inches

L/300 (0.56 inches) does not correspond to a standard CBC deflection limit category. It falls between L/240 and L/360 but is not a prescribed value in CBC Table 1604.3 for floor joists. Selecting it reflects guessing between two memorized values.

Option D: L/180 = 0.93 inches

L/180 (0.93 inches) is the deflection limit for roof members not supporting a plaster ceiling, under live load or wind load. It is less restrictive than the floor joist standard and would allow excessive bounce and serviceability issues in a residential floor.

Memory Technique

Remember the deflection hierarchy: L/360 for glass/plaster (fragile), L/240 for floors (firm footing), L/180 for roofs (can flex more). Think '360 degrees = full circle of protection for fragile things; 240 = solid floor standard; 180 = roof can breathe.'

Was this explanation helpful?

More California Questions

A contractor is installing shear walls in a residence located in Seismic Design Category D. The engineer's plans call for 15/32-inch structural sheathing with 8d nails at 6 inches on center at panel edges. The contractor wants to substitute 7/16-inch OSB with the same nailing. Is this substitution acceptable?

You are reviewing plans for a mixed-use building where the ground floor will house a restaurant with commercial kitchen equipment. The architect has specified standard residential electrical requirements throughout. What Title 24 compliance issue should you identify?

According to CBC seismic provisions, what is the concept behind the 'strong column, weak beam' design philosophy?

A residence in California has 2,800 sq ft of conditioned space. The HVAC system efficiency is 16 SEER. What is the approximate Title 24 compliance margin compared to the minimum 14 SEER requirement?

You're constructing a foundation on liquefiable soils identified in a California coastal area. The geotechnical report recommends deep foundations. Which option is most commonly specified?

A contractor is installing a heat recovery ventilation (HRV) system to comply with Title 24. The system serves a 2,000 sq ft house with 3 bedrooms. What is the minimum required ventilation rate?

During construction of a basement in sandy soil conditions, you encounter groundwater at 4 feet below grade. The basement extends 8 feet below grade. What is the critical design consideration per CBC?

During a seismic retrofit project, you discover that existing concrete has a compressive strength of 2,200 psi. The engineer specifies new anchor bolts that require 2,500 psi minimum concrete strength. What is the most appropriate action?

What is the maximum allowable notch depth in a 2x10 floor joist per CBC requirements?

You're reviewing plans for a wood-framed structure in seismic design category D. The project calls for a shear wall with 15/32-inch structural sheathing and 8d nails spaced 6 inches on center at panel edges. What is the allowable shear value per the CBC?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.