A building is classified as Seismic Design Category D. According to CBC, what is the required redundancy factor (ρ) for the seismic force-resisting system if the building has adequate redundancy?
Correct Answer
C) ρ = 1.0
When a building has adequate redundancy in its seismic force-resisting system, the redundancy factor ρ = 1.0. If redundancy is inadequate, ρ = 1.3 is used to increase design forces.
Why This Is the Correct Answer
CBC (ASCE 7 as adopted) defines two values for the redundancy factor ρ: 1.0 when the seismic force-resisting system is deemed to have adequate redundancy (sufficient lateral load paths so that removing any single element does not reduce story strength by more than 33%), and 1.3 when redundancy is inadequate. For SDC D with adequate redundancy, ρ = 1.0.
Why the Other Options Are Wrong
Option A: ρ = 1.5
ρ = 1.5 is not a code-defined value in the CBC/ASCE 7 redundancy factor framework. This value does not appear in the standard; selecting it indicates confusion with other load factors or older code editions.
Option B: ρ = 1.3
ρ = 1.3 applies when the building does NOT have adequate redundancy in SDC D, E, or F — the opposite of the scenario described. The question explicitly states adequate redundancy, so 1.3 is incorrect here.
Option D: ρ = 2.0
ρ = 2.0 is not a standard code value for the redundancy factor. It may be confused with strength reduction factors or overstrength factors (Ω₀) used in seismic design, but it does not apply here.
Memory Technique
Think of redundancy as a safety net: if you have a good net (adequate redundancy), the penalty is zero — multiply by 1.0, which changes nothing. If your net has holes (inadequate redundancy), you pay the 1.3 penalty. 'Adequate = 1.0, Inadequate = 1.3.'
More California Questions
A contractor is installing shear walls in a residence located in Seismic Design Category D. The engineer's plans call for 15/32-inch structural sheathing with 8d nails at 6 inches on center at panel edges. The contractor wants to substitute 7/16-inch OSB with the same nailing. Is this substitution acceptable?
You are reviewing plans for a mixed-use building where the ground floor will house a restaurant with commercial kitchen equipment. The architect has specified standard residential electrical requirements throughout. What Title 24 compliance issue should you identify?
According to CBC seismic provisions, what is the concept behind the 'strong column, weak beam' design philosophy?
A residence in California has 2,800 sq ft of conditioned space. The HVAC system efficiency is 16 SEER. What is the approximate Title 24 compliance margin compared to the minimum 14 SEER requirement?
You're constructing a foundation on liquefiable soils identified in a California coastal area. The geotechnical report recommends deep foundations. Which option is most commonly specified?
A contractor is installing a heat recovery ventilation (HRV) system to comply with Title 24. The system serves a 2,000 sq ft house with 3 bedrooms. What is the minimum required ventilation rate?
During construction of a basement in sandy soil conditions, you encounter groundwater at 4 feet below grade. The basement extends 8 feet below grade. What is the critical design consideration per CBC?
During a seismic retrofit project, you discover that existing concrete has a compressive strength of 2,200 psi. The engineer specifies new anchor bolts that require 2,500 psi minimum concrete strength. What is the most appropriate action?
What is the maximum allowable notch depth in a 2x10 floor joist per CBC requirements?
You're reviewing plans for a wood-framed structure in seismic design category D. The project calls for a shear wall with 15/32-inch structural sheathing and 8d nails spaced 6 inches on center at panel edges. What is the allowable shear value per the CBC?