A commercial ice machine uses a remote air-cooled condenser connected by a line set that was brazed during installation, and the completed circuit holds about nine pounds of refrigerant. Which certification covers service on that circuit?
Correct Answer
A) Type II, because the circuit was assembled in the field and holds more than five pounds
This machine fails the small appliance test twice over. The refrigerant circuit was completed on the job site rather than sealed at the factory, and the charge is above the five-pound ceiling. Either failure alone would take it out of Type I; together they put it clearly in the field-assembled high-pressure class that Type II covers. Note that a different ice machine, one that arrives self-contained and factory sealed with a charge under the limit, would be Type I. The same product name can land in either category depending on how the unit is built and piped.
Why This Is the Correct Answer
Small appliance status requires factory manufacture, factory charge, factory hermetic seal, and five pounds or less. A remote-condenser ice machine is field piped and field charged and exceeds the charge limit, so it is a high-pressure appliance and Type II applies.
Why the Other Options Are Wrong
Option B: Type I, because ice machines are listed as small appliances no matter how they are piped
No equipment is small-appliance by product name. Self-contained ice makers often qualify, but a field-piped remote system does not, because the circuit was never sealed at the factory.
Option C: Type III, because the equipment serves a food service refrigeration load
Type III is for low-pressure appliances whose refrigerant boils above room temperature. The application the equipment serves has nothing to do with the pressure class.
Option D: Type I, because the nine-pound charge is divided between two separate sections
The charge limit applies to the appliance, not to individual sections of it. Splitting a circuit across two locations does not split its charge for classification purposes.
Memory Technique
Remote condenser means remote from Type I. If a line set crosses the building, it is Type II.
Reference Hint
40 CFR 82.152 small appliance definition: factory manufactured, charged and hermetically sealed, 5 lbs or less. Field-piped equipment above that limit is Type II under 40 CFR 82.161.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A technician is pulling the remaining vapor charge out of a high-pressure system with a recovery machine and wants the job to move as fast as it safely can. Where should the recovery hoses be connected?
Next Question
Type III certification exists as a class of its own, separate from the equipment that Type II covers. What is it about a low-pressure appliance that puts it in that separate class?