One machine in the plant room is a seven-hundred-ton centrifugal chiller charged with R-134a, and the machine beside it is a centrifugal chiller charged with R-123. Which certification covers work on the R-134a machine?

Correct Answer

D) Type II, because R-134a keeps the machine above atmospheric pressure no matter how large it is

Certification class follows the refrigerant, not the tonnage or the compressor style. R-134a boils well below room temperature at atmospheric pressure, so a machine charged with it runs above atmospheric pressure and belongs to the high-pressure class covered by Type II. The neighboring machine using R-123 is low pressure and needs Type III. Two identical-looking centrifugal chillers side by side can therefore require two different certifications. Size, tonnage and compressor type are all distractions; the question to answer is what the refrigerant does at atmospheric pressure.

Answer Options
A
Type III, because a centrifugal chiller of that tonnage is always handled as a low-pressure machine
B
Universal, because a plant room holding more than one pressure class requires it
C
Type I, because the whole charge stays inside one factory-built package
D
Type II, because R-134a keeps the machine above atmospheric pressure no matter how large it is

Why This Is the Correct Answer

The definitions sort appliances by the atmospheric boiling point of the refrigerant charged into them. R-134a sits in the high-pressure band, so the chiller is a high-pressure appliance and Type II is the required certification. Nothing in the definitions references capacity, footprint or compressor design.

Why the Other Options Are Wrong

Option A: Type III, because a centrifugal chiller of that tonnage is always handled as a low-pressure machine

Tonnage is not part of any appliance definition. A large machine charged with a high-pressure refrigerant is still a high-pressure appliance, and low pressure is not a synonym for large.

Option B: Universal, because a plant room holding more than one pressure class requires it

Universal is convenient for a technician who works on everything, but the R-134a machine by itself only requires Type II. The question asks what that one machine needs.

Option C: Type I, because the whole charge stays inside one factory-built package

Type I is limited to factory-sealed appliances holding five pounds or less. A seven-hundred-ton chiller is field assembled and holds hundreds of pounds.

Memory Technique

Read the nameplate refrigerant, not the tonnage. Big does not mean low pressure.

Reference Hint

Class is set by the refrigerant's boiling point at atmospheric pressure, 40 CFR 82.152. R-134a is high pressure and needs Type II; R-123 is low pressure and needs Type III.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.