A full nitrogen cylinder can sit at well over two thousand pounds per square inch, while the components in a comfort cooling system are rated for a small fraction of that. What does that difference require of the technician?
Correct Answer
A) The cylinder must be fed through a pressure regulator so only a controlled test pressure ever reaches the system
Cylinder pressure is not something a technician can control by hand. A cylinder valve is either open or closed, and opening it slowly on a full nitrogen bottle still delivers full cylinder pressure to whatever is downstream, just a moment later. A regulator is the device that steps that pressure down and holds a set outlet pressure regardless of what the cylinder is doing. Without one, a system can be over-pressurized in a second, rupturing a component or lifting a relief device with the technician standing next to it.
Why This Is the Correct Answer
A regulator is a pressure-reducing device with a set outlet. It maintains the pressure the technician dialed in even as cylinder pressure falls, which is the only reliable way to keep a huge supply pressure from reaching equipment rated for far less.
Why the Other Options Are Wrong
Option B: The cylinder valve should be cracked open slowly instead, since opening it gradually limits the pressure delivered
A valve controls flow, not pressure. Opening it slowly changes how fast the system fills, not the pressure it eventually reaches, which is full cylinder pressure.
Option C: The nitrogen should be discharged into a length of hose first so it loses pressure before entering the system
Gas does not lose pressure by traveling through a hose. A hose full of high-pressure nitrogen simply delivers high-pressure nitrogen at the other end, and the hose itself may not be rated for it.
Option D: The system should be left connected to the recovery machine so the machine can absorb any excess pressure
A recovery machine is not a relief device and is not rated to absorb cylinder pressure. Connecting it in that situation puts the machine at risk too.
Memory Technique
A valve controls how fast, a regulator controls how hard. You need the regulator.
Reference Hint
Dry nitrogen must be delivered through a pressure regulator; cylinder pressure vastly exceeds system component ratings.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A technician is trying to use soap bubble solution to locate a leak on a rooftop unit on a windy and hot afternoon. What limits that method under those conditions?
Next Question
A technician is sweeping an electronic leak detector along the brazed joints of an R-134a rack looking for a small leak. How should the probe be handled to give the best chance of finding it?