A shop owns a single stage vacuum pump and a two stage vacuum pump of the same displacement. What does the second stage of the two stage pump give the technician?
Correct Answer
B) A deeper ultimate vacuum than the single stage pump can reach
In a two stage pump the gas discharged by the first stage is handed to a second stage before it reaches atmosphere, so the first stage never has to work against full atmospheric pressure. That lets the pump keep moving vapor at pressures where a single stage pump stalls, and the ultimate vacuum it can reach is much deeper. Displacement is a separate rating, and neither pump may ever be used to remove refrigerant from a charged system.
Why This Is the Correct Answer
The second stage takes the discharge of the first, so the first stage works against a much lower back pressure and can keep pulling vapor down to a far lower pressure. The result is a deeper ultimate vacuum, which matters when the goal is to boil moisture out of a system that has been open. Displacement, measured in cubic feet per minute, sets how fast the pump gets there and is a separate specification.
Why the Other Options Are Wrong
Option A: A higher displacement rating measured in cubic feet per minute
Staging changes how deep a pump can pull, not how much volume it moves. Two pumps of the same displacement move the same volume at the start.
Option C: The ability to recover refrigerant as well as pull a vacuum
No vacuum pump may be used to remove refrigerant from a charged appliance regardless of how many stages it has. That is recovery equipment work.
Option D: A built in filter that keeps moisture out of the pump oil
Neither design filters the oil. Moisture drawn out of a system dissolves into vacuum pump oil, which is why the oil is changed after wet jobs.
Memory Technique
Two stages, two chances to squeeze. The second stage means the first never fights the whole atmosphere.
Reference Hint
A two stage vacuum pump reaches a deeper ultimate vacuum; displacement in cubic feet per minute is a separate rating.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
Next Question
A semi-hermetic compressor that has been opened for valve plate work twice now shows an oil film along the seam between the head and the body. What should the technician do about that joint?