A pressure relief valve on a rack receiver lifted during a hot spell and has been losing refrigerant slowly ever since, even though system pressure is now normal. What is the correct repair?

Correct Answer

C) Replace the relief valve, because a valve that has discharged may not reseat

A pressure relief valve is designed to open once and protect the vessel, and it is not guaranteed to seal again afterward. Debris carried past the seat, or distortion of the seat itself, leaves a path that weeps continuously. Adjusting a relief valve destroys its set pressure and its listing, and capping the outlet defeats the safety device entirely. The valve is a replacement item once it has discharged.

Answer Options
A
Tighten the valve down against its seat until the weeping stops
B
Leave it in service, since it will reseat once cooler weather returns
C
Replace the relief valve, because a valve that has discharged may not reseat
D
Cap the valve outlet so the escaping refrigerant is contained in the system

Why This Is the Correct Answer

Relief valves are not designed to reseal reliably after they have relieved. Anything that passed the seat can hold it open, and the seat can deform under the discharge. A weeping valve is therefore replaced rather than adjusted, which restores both a tight refrigerant circuit and a working overpressure protection for the receiver.

Why the Other Options Are Wrong

Option A: Tighten the valve down against its seat until the weeping stops

Adjusting a relief valve changes the pressure at which it protects the vessel and voids its listing. It is not a field-adjustable component.

Option B: Leave it in service, since it will reseat once cooler weather returns

The weep will continue in any weather, because it is caused by a damaged or fouled seat rather than by current system pressure.

Option D: Cap the valve outlet so the escaping refrigerant is contained in the system

Capping the outlet disables the vessel's overpressure protection. That converts a refrigerant loss into the possibility of a receiver rupture.

Memory Technique

A relief valve is a one-shot bodyguard. Once it takes the hit, it retires.

Reference Hint

A pressure relief valve that has discharged may not reseat tightly and should be replaced rather than adjusted or capped.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.