A small diameter equalizer tube on a rack is found weeping refrigerant exactly where it crosses a steel frame member, with the copper worn bright and thin at that point. What has caused the leak?
Correct Answer
B) Vibration wearing the tube wall away where it rubs against the steel
A compressor running on a rack shakes everything attached to it. Where a small tube touches a rigid frame member the two surfaces work against each other thousands of times an hour, and the copper, being softer, gives up material until the wall is thin enough to open. The bright polished patch is the signature. The repair is to fix the leak and then isolate the tube from the frame with a grommet or a clamp so the rubbing cannot start again.
Why This Is the Correct Answer
Vibration from the compressor causes the tube to move against the steel frame, and the softer copper wears away at the contact point. The bright, thinned area is exactly what abrasion leaves behind. Repairing the tube without separating it from the frame guarantees the same failure again, so the fix includes cushioning or reclamping the line.
Why the Other Options Are Wrong
Option A: Galvanic action between the copper tube and the steel frame member
Galvanic corrosion needs an electrolyte bridging the two metals and leaves a rough corroded surface, not a bright polished wear patch.
Option C: Heat conducted from the frame gradually annealing the copper wall
A frame member sits at the same temperature as everything around it. Nothing on a rack conducts enough heat into a tube to anneal it through.
Option D: Overpressure stretching the tube where the frame restrained it
Overpressure would bulge or split the tube along its weakest section, and it would not selectively thin the wall at a single contact point.
Memory Technique
Copper against steel, all day, every day. Steel always wins.
Reference Hint
Vibration rub-through occurs where refrigerant tubing contacts rigid structure; the repair includes isolating the tube.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A technician has finished locating and repairing a leak on a large commercial refrigeration system. What belongs in the service record for that visit?
Next Question
A system loses part of its charge over the course of several months, but a careful search during a service call turns up nothing at all. Which detection approach fits that situation best?