A rack uses an open drive compressor with a motor mounted alongside and a belt between them. Which point on that compressor is the one most likely to leak refrigerant?
Correct Answer
D) The shaft seal where the crankshaft passes out of the housing
An open drive compressor has a rotating shaft leaving the pressurized housing, and the seal around that shaft is the one part of the refrigerant circuit with a moving surface running against a stationary one. It wears, it depends on an oil film to stay tight, and it leaks more when the machine sits idle and the film drains away. Gaskets and flanges on the same compressor leak far less often because nothing moves across them.
Why This Is the Correct Answer
The shaft seal is a dynamic seal, the only place on the compressor where refrigerant is held back by surfaces sliding against one another. Wear, loss of the oil film during long idle periods and misalignment of the drive all cause it to weep. Every other joint on the compressor is static and, once made up properly, stays tight far longer.
Why the Other Options Are Wrong
Option A: The suction service valve flange where it bolts to the body
Service valve flanges are static joints with a gasket and bolts. They can leak after being disturbed, but they are not the usual suspect on a running machine.
Option B: The oil sight glass fitted into the side of the crankcase
A sight glass is threaded or bolted into the crankcase with a gasket. It sits in a low pressure part of the compressor and rarely fails first.
Option C: The head gasket between the valve plate and the cylinder head
Head gaskets do fail, usually after overheating, but they are clamped static joints and are not the everyday leak point on an open drive machine.
Memory Technique
Moving parts leak, still parts hold. Find the part that turns and start there.
Reference Hint
The shaft seal is the usual leak point on an open drive compressor, since it is the only dynamic seal in the circuit.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A system has been open to the atmosphere for two days before its repair was completed. Beyond slowing the equipment down, what does moisture left in a running refrigeration system cause?
Next Question
A technician is pulling the remaining vapor charge out of a high-pressure system with a recovery machine and wants the job to move as fast as it safely can. Where should the recovery hoses be connected?