A low-temperature system is undercharged enough that the low side operates below atmospheric pressure whenever the compressor runs. What happens at a leak on that part of the system?
Correct Answer
D) Air and moisture are pulled into the system instead of refrigerant leaking out, so a detector finds nothing while the unit runs
Gas moves from high pressure to low pressure. When the low side sits below atmospheric, the outside air is at the higher pressure, so the flow at a leak reverses and air with its water vapor is drawn into the system. A detector sweeping that joint finds nothing, bubble solution gets sucked in rather than blown out, and the technician can spend an afternoon proving there is no leak on the very section that is leaking. The way to find it is to shut the unit down and pressurize the system, usually with dry nitrogen, so flow goes outward again.
Why This Is the Correct Answer
Direction of flow follows the pressure difference. A section below atmospheric pressure has the outside air at the higher pressure, so anything moving through the opening moves inward. That is why nothing escapes to be detected and why the system accumulates air, moisture and eventually acid.
Why the Other Options Are Wrong
Option A: Refrigerant escapes there faster than it would from an identical opening on the high side, because the low side is moving more vapor
Nothing escapes from a section sitting below atmospheric pressure. Flow at that opening runs inward, and it is the high side, above atmospheric, where refrigerant is actually pushed out of the system.
Option B: The leak seals itself while the unit runs, because the tubing is drawn inward around the opening by the vacuum
Copper tubing is rigid, and a pressure difference does not close a hole in it. The opening stays exactly the size it was, which is why air keeps coming in for as long as the unit runs.
Option C: Soap bubbles form quickly at the leak, because the vapor crossing the opening is moving faster than it would elsewhere
With flow moving inward, soap solution is drawn into the opening rather than blown into a bubble. It is one of the more misleading results a technician can get, because it reads as a sound joint.
Memory Technique
Vacuum sucks, pressure blows. A leak in a vacuum is an inlet, not an outlet.
Reference Hint
Leak detection requires the section under test to be above atmospheric pressure; 40 CFR Part 82, Subpart F governs repair and verification.
More epa-608-type-2 Questions
A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?
An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?
A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?
A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?
On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?
A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?
A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?
A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?
Next Question
A large appliance has been recovered down to fifteen inches of mercury vacuum and a brazed joint now has to be heated and taken apart. Why do technicians raise the system back to atmospheric pressure with dry nitrogen first?