A small leak is suspected somewhere inside an evaporator coil, in tubing buried among the fins and the rows of the bundle. What makes that kind of leak so hard to pin down?

Correct Answer

B) Airflow through the coil and the depth of the tube bundle scatter escaping vapor before a probe can pick it up

Two things work against the technician here. The blower moves a large volume of air across the coil and dilutes escaping vapor to nothing, and the leak may be several rows deep where no probe can reach. The practical approach is to shut the blower off and let the coil sit so vapor can collect, then probe the underside and downstream face slowly. If that fails, dye and a return visit or an isolated nitrogen pressure test on the coil alone will settle it. Corrosion pinholes in coil tubing are a common failure on older equipment.

Answer Options
A
Coil leaks only open up while the system is shut down, so no test run with the unit going will find them
B
Airflow through the coil and the depth of the tube bundle scatter escaping vapor before a probe can pick it up
C
The aluminum fins shield the tubing so an electronic detector cannot sense refrigerant anywhere inside the bundle
D
Evaporator coils always operate under a vacuum, so nothing ever escapes from them to be detected

Why This Is the Correct Answer

Detection depends on refrigerant vapor concentrating near the leak long enough to be sensed. Moving air destroys that concentration, and a leak buried in the middle of a tube bundle is physically inaccessible to a probe tip, so both the chemistry and the geometry work against a quick find.

Why the Other Options Are Wrong

Option A: Coil leaks only open up while the system is shut down, so no test run with the unit going will find them

A leak is a hole and it does not open and close with the unit's operating state. Pressure changes make one easier or harder to find, which is not the same as being undetectable.

Option C: The aluminum fins shield the tubing so an electronic detector cannot sense refrigerant anywhere inside the bundle

Fins do not block a detector chemically; they block the probe physically and the moving air dilutes the sample. Treating aluminum as a shield swaps an access problem for an instrument problem.

Option D: Evaporator coils always operate under a vacuum, so nothing ever escapes from them to be detected

An evaporator on a properly charged high-pressure system runs above atmospheric pressure. Only a badly undercharged low-temperature system pulls its low side down into a vacuum.

Memory Technique

Moving air hides leaks. Kill the fan and let the vapor puddle.

Reference Hint

Leaks must be located, repaired and verified under 40 CFR Part 82, Subpart F. Isolating a coil for a nitrogen test is standard practice.

Was this explanation helpful?

More epa-608-type-2 Questions

A walk-in cooler condensing unit holds a full charge of twenty-five pounds of R-404A, which is below the fifty pound threshold that brings an appliance under the leak repair provisions. What still applies to this unit?

An office building has thirty water source heat pumps on a common water loop, and each one left the factory assembled, hermetically sealed and charged with four pounds of R-410A. How is one of those units classified?

A data sheet for an unfamiliar refrigerant lists a boiling point of about fifty-five degrees Fahrenheit at atmospheric pressure. What does that tell a technician holding Core and Type II certification?

A technician holds Core, Type I and Type III certification and is sent to recover the charge from a twenty ton rooftop unit charged with R-410A. What does that combination of sections allow on this job?

A fleet garage technician holds only the vehicle air conditioning certification issued under Section 609 and is asked to recover the charge from the shop's own rooftop air conditioner. What does that credential allow?

A split system's outdoor unit, indoor coil and the line set the installer ran and brazed between them are being considered. For the purposes of the refrigerant rules, what makes up the appliance here?

On a new installation the line set is brazed to a factory charged outdoor unit and an indoor coil shipped under a nitrogen holding charge, with the outdoor unit's service valves still closed. What does the recovery requirement call for before that brazing?

A rooftop unit's data plate has weathered until the charge figure cannot be read, and the technician needs the full charge to place the appliance under the evacuation and leak provisions. Where should that figure come from?

A computer room air conditioning unit holds forty pounds of R-407C and connects to a remote air cooled condenser through refrigerant piping run and brazed by the installer. How is that unit classified?

A shop's office manager, who holds no technician certification, is sent to a supply house to pick up a new recovery machine for the commercial crew. What does the sales restriction require at that counter?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.