A helper suggests filling an empty recovery cylinder with dry nitrogen from the shop bottle so it can be carried to jobs as a portable supply of test gas. What is wrong with that idea?

Correct Answer

A) A recovery cylinder is rated for refrigerant service, not for a high pressure nitrogen fill

A recovery cylinder is a pressure vessel built and stamped for a particular service pressure, commonly four hundred pounds per square inch. A nitrogen cylinder leaves the gas supplier at a couple of thousand pounds. Transferring from one to the other means either an unregulated fill that can burst the recovery cylinder, or a partial fill that gives so little usable nitrogen it defeats the purpose. Cylinders are filled by the gas supplier for the service they are marked for, and a recovery cylinder is marked for refrigerant.

Answer Options
A
A recovery cylinder is rated for refrigerant service, not for a high pressure nitrogen fill
B
A recovery cylinder would work but has to be relabelled before the nitrogen goes into it
C
A recovery cylinder cannot hold nitrogen because its valve passes only liquid refrigerant
D
A recovery cylinder must be evacuated first, after which the transfer is acceptable

Why This Is the Correct Answer

The service pressure stamped on a recovery cylinder is the limit it was designed and tested to. Nitrogen is stored and supplied at pressures many times higher, so filling a refrigerant cylinder from a nitrogen bottle is either dangerous or pointless depending on how it is done. Cylinders are filled by suppliers for the gas and the service they are marked for, and mixing services is never a field operation.

Why the Other Options Are Wrong

Option B: A recovery cylinder would work but has to be relabelled before the nitrogen goes into it

Labelling addresses what a cylinder contains. It does nothing about a pressure rating, which is fixed by how the vessel was built.

Option C: A recovery cylinder cannot hold nitrogen because its valve passes only liquid refrigerant

Cylinder valves handle gas or liquid according to the dip tube arrangement, and this is not what makes the idea unsafe.

Option D: A recovery cylinder must be evacuated first, after which the transfer is acceptable

Evacuating deals with contamination. The objection here is the pressure rating, which evacuation does not change in any way.

Memory Technique

The stamp on the collar is not a suggestion.

Reference Hint

Cylinders are used only for the gas and service pressure they are marked for. Recovery cylinders hold recovered refrigerant, nothing else.

Was this explanation helpful?

More epa-608-type-1 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.