Recovery has brought a small appliance down to four inches of mercury vacuum, and the technician is about to cut the lines and braze in a new compressor. What should be done about the system pressure first?
Correct Answer
B) Bring it back with dry nitrogen to a slight positive pressure before anything is opened
A system left in a vacuum draws room air, and with it moisture, inward the moment the tubing is opened. Bringing the pressure back up with dry nitrogen to just above atmospheric means the flow at the open end runs outward instead, keeping the inside dry and giving the brazing purge something to work with. Shop compressed air is the wrong gas entirely: it carries water and oil from the compressor, and air in a system that will later be charged is a non condensable that has to be pulled back out.
Why This Is the Correct Answer
Breaking the vacuum with dry nitrogen puts the system slightly above room pressure, so when the tubing is cut the gas flows out rather than pulling humid room air in. It also sets up the purge that will run through the joints during brazing. Nitrogen is dry, inert and leaves nothing behind, which is exactly what a system about to be sealed for a decade needs.
Why the Other Options Are Wrong
Option A: Leave it in the vacuum, so any leak during brazing pulls inward rather than pushing out
A vacuum does not stay a vacuum once the tube is cut. It equalizes instantly by pulling room air, moisture and dust into the very system that is about to be closed up.
Option C: Bring it up with shop air, which is free and holds the joint clear while it is heated
Shop air carries water vapor and compressor oil mist, and its oxygen is what causes the oxide scale that the brazing purge exists to prevent.
Option D: Leave it in the vacuum and open the line quickly so little room air has time to enter
Room air enters at the speed of sound the moment the tube is opened. Working quickly does not change the outcome, and the system stays open for the whole repair anyway.
Memory Technique
Positive pressure blows dirt out. A vacuum sucks it in.
Reference Hint
Break the vacuum with dry nitrogen to slightly above atmospheric before opening a system for repair.
More epa-608-type-1 Questions
An under-counter ice maker is one factory-sealed cabinet, while a modular ice machine head is joined to a remote condenser by field-run tubing. What certification does servicing the modular machine's circuit require?
A technician recovers refrigerant from a small appliance using a recovery machine that was manufactured in 1991. What recovery level must that older equipment achieve?
Two technicians recover from identical refrigerators with working compressors, one using a 1991 recovery machine and the other a 2015 machine. Why do their required recovery levels differ?
System-dependent recovery equipment may be used only on appliances that normally hold up to what amount of refrigerant?
What feature defines a self-contained recovery unit and sets it apart from the system-dependent kind?
When system-dependent recovery equipment is used on a small appliance whose compressor still runs, how can that working compressor be put to use?
Recovery from a small appliance has slowed down and the pressure is barely moving. What accepted technique helps drive the remaining refrigerant out?
After the recovery unit stops pulling on a small appliance, how does a technician confirm that the recovery is actually complete?
A sealed small appliance offers no service port at all. What has to happen before recovery equipment can be connected to it?
As refrigerant from a string of small appliances collects in a recovery cylinder, what fill limit applies to that cylinder?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A superintendent pulls twenty window air conditioners out of the walls every October, stores them in a basement, and reinstalls the same units the following May. What do the recovery rules require at the time the units are removed?
Next Question
A wholesaler is about to sell a cylinder of refrigerant to a walk-in customer. What does the refrigerant sales restriction require of that seller?