An industrial facility has a 440-volt, three-phase, low-speed NEMA Design B squirrel-cage motor with a nameplate full-load current of 100 amperes. For this motor, 2026 NEC 430.6 requires the nameplate current as the sizing basis. It is not Design BE or CE. An inverse-time circuit breaker will provide branch-circuit short-circuit and ground-fault protection. Under the ordinary Table 430.52(C)(1) percentage, before any permitted increase for starting current and with no other exception, what is its maximum rating?
- A125A
- B100A
- C80A
- 250A
Where to look it up
https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec
Why D is correct
100 A × 250% = 250 A, D. The inverse-time breaker percentage establishes this ordinary branch short-circuit/ground-fault protection maximum, not a universal 125% minimum. Smaller ratings do not equal the requested maximum and still must carry starting current if selected. Separate motor overload protection uses a different rule; it cannot be replaced by this breaker-sizing calculation. Source: E Light Electric, Motor and Welding Machine Calculation Steps 2026 NEC, current-basis rule and Step 3: https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec