An industrial facility has a 440V, 3-phase motor with a full-load current of 100A. What is the minimum overcurrent protection required for this motor, according to 430.52(A)(1)?
- 125A
- B100A
- C80A
- D150A
Exam tip
Remember that the overcurrent protection for motors must be at least 125% of the full-load current.
Why A is correct
According to 430.52(A)(1), the overcurrent protection for a motor must not be less than 125% of the motor's full-load current. Therefore, 125% of 100A is 125A, which is the minimum required overcurrent protection.