An industrial facility has a 440-volt, three-phase, low-speed NEMA Design B squirrel-cage motor with a nameplate full-load current of 100 amperes. For this motor, 2026 NEC 430.6 requires the nameplate current as the sizing basis. It is not Design BE or CE. An inverse-time circuit breaker will provide branch-circuit short-circuit and ground-fault protection. Under the ordinary Table 430.52(C)(1) percentage, before any permitted increase for starting current and with no other exception, what is its maximum rating?

Texas Master exam practice question · Calculations & Theory

An industrial facility has a 440-volt, three-phase, low-speed NEMA Design B squirrel-cage motor with a nameplate full-load current of 100 amperes. For this motor, 2026 NEC 430.6 requires the nameplate current as the sizing basis. It is not Design BE or CE. An inverse-time circuit breaker will provide branch-circuit short-circuit and ground-fault protection. Under the ordinary Table 430.52(C)(1) percentage, before any permitted increase for starting current and with no other exception, what is its maximum rating?

  • A125A
  • B100A
  • C80A
  • 250A

Where to look it up

https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec

Why D is correct

100 A × 250% = 250 A, D. The inverse-time breaker percentage establishes this ordinary branch short-circuit/ground-fault protection maximum, not a universal 125% minimum. Smaller ratings do not equal the requested maximum and still must carry starting current if selected. Separate motor overload protection uses a different rule; it cannot be replaced by this breaker-sizing calculation. Source: E Light Electric, Motor and Welding Machine Calculation Steps 2026 NEC, current-basis rule and Step 3: https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec

Practice 6 more Calculations & Theory questions

Timed mock exams, a wrong book and flashcards — one subscription covers every contractor exam line.

Start studying free