A feeder overcurrent device is rated higher than the allowable ampacity of its conductors, with no applicable tap or next-size rule. What is required?

Texas Journeyman exam practice question · Feeders

A feeder overcurrent device is rated higher than the allowable ampacity of its conductors, with no applicable tap or next-size rule. What is required?

  • Reduce the device rating or increase conductor ampacity
  • BLeave it because feeders are never protected at their supply end
  • CRelabel the conductors with a higher temperature
  • DIncrease only the equipment-grounding conductor

Why A is correct

Feeder conductors require overcurrent protection coordinated with their allowable ampacity unless a specific permission applies. Relabeling field insulation or changing an unrelated grounding conductor does not protect undersized current-carrying conductors.