A conductor begins at 75 amperes in the permitted insulation column. Supplied adjustment and correction factors are 80 percent and 91 percent. What ampacity results before terminal limitations?
- A73.2 amperes
- B60.0 amperes
- 54.6 amperes
- D68.3 amperes
Why C is correct
Apply both supplied factors to the starting ampacity: 75 × 0.80 × 0.91 = 54.6 amperes. Terminal and equipment limitations must then be checked separately.