A feeder supplies 70 amperes of noncontinuous load and 40 amperes of continuous load. Ignoring other factors, what minimum calculated ampacity is required?

Texas Journeyman exam practice question · Feeder Calculations

A feeder supplies 70 amperes of noncontinuous load and 40 amperes of continuous load. Ignoring other factors, what minimum calculated ampacity is required?

  • A88 amperes
  • 120 amperes
  • C110 amperes
  • D137.5 amperes

Why B is correct

The continuous load contributes 40 times 1.25, or 50 amperes. Adding the 70-ampere noncontinuous load produces a feeder calculation of 120 amperes.