A 30-kilovolt-ampere three-phase transformer has a 208-volt secondary. Using 1.732, approximately what full-load secondary current results?

Texas Journeyman exam practice question · Equipment & Devices

A 30-kilovolt-ampere three-phase transformer has a 208-volt secondary. Using 1.732, approximately what full-load secondary current results?

  • A144.2 amperes
  • B48.1 amperes
  • 83.3 amperes
  • D6,240 amperes

Why C is correct

Three-phase current equals volt-amperes divided by 1.732 and line voltage. Dividing 30,000 by 1.732 and then by 208 gives approximately 83.3 amperes.