A classroom measurement gives 300 cfm of outdoor air and a room volume of 9,000 ft³. What outdoor-air change rate results?

Texas ACR A exam practice question · Texas Laws & Rules

A classroom measurement gives 300 cfm of outdoor air and a room volume of 9,000 ft³. What outdoor-air change rate results?

  • A0.033 ACH
  • 2 ACH
  • C30 ACH
  • D1,800 ACH

Where to look it up

https://www.cdc.gov/niosh/ventilation/faq/index.html

Why B is correct

300 × 60 / 9,000 = 2 ACH. The 60 converts minutes to hours. This is a measured-rate calculation, not a Texas classroom minimum.