Under unamended 2021 IPC Section 1002.4.1.1, which arrangement provides the specified potable-water-supplied trap seal protection for an emergency floor drain?

Plumber exam practice question · Traps, Interceptors & Separators

Under unamended 2021 IPC Section 1002.4.1.1, which arrangement provides the specified potable-water-supplied trap seal protection for an emergency floor drain?

  • An ASSE 1018 trap seal primer valve discharging to the trap’s inlet side above the trap seal
  • BA spring-loaded check valve in the trap outlet with no primer supply
  • CA deeper trap seal used alone, without any recognized seal-protection method
  • DA loose cleanout plug that admits room air to the drain

Where to look it up

https://www.ncosfm.gov/b-1-2024-ncpc/open

Why A is correct

Section 1002.4.1.1 requires a potable-water-supplied primer conforming to ASSE 1018 and an inlet-side discharge connection above the trap seal. This replaces water lost through evaporation. Other recognized methods have their own standards and installation conditions. In particular, Section 1002.4.1.5 allows a lavatory/hand-sink drain connection for specified receiving fixtures in the same room; its adjacent-room allowance concerns the drinking-fountain connection, not every source fixture. Neither extra seal depth nor a loose plug substitutes for a recognized method. See PDF p.140. Reference: unamended 2021 IPC base text reproduced in the official OSFM comparison, https://www.ncosfm.gov/b-1-2024-ncpc/open