An electrician proposes hanging a luminaire directly from an ordinary PVC electrical conduit run in a covered walkway. Under 2023 NEC 352.12(B), is this a permitted use of the conduit?

Electrician exam practice question · Wiring Methods & Materials

An electrician proposes hanging a luminaire directly from an ordinary PVC electrical conduit run in a covered walkway. Under 2023 NEC 352.12(B), is this a permitted use of the conduit?

  • AYes, if the conduit is trade size 1 or larger and strapped on both sides
  • BYes, if the luminaire weighs less than 6 pounds
  • No; directly supporting the luminaire is a prohibited use of the PVC conduit
  • DYes, if Schedule 80 PVC replaces Schedule 40

Where to look it up

https://docinfofiles.nfpa.org/files/AboutTheCodes/70/70_A2025_NEC_P08_FD_PIResponses.pdf

Why C is correct

Section 352.12(B) prohibits using PVC conduit to support luminaires. Trade size, fixture weight and Schedule 80 wall thickness do not create the claimed permissions. The limited conduit-body support permission in 352.10(I) is separate and does not allow those bodies to support luminaires. Source: 2023 baseline text in NFPA Public Inputs 2256 and 2179, PDF pages 199 and 198 (printed 174 and 173). https://docinfofiles.nfpa.org/files/AboutTheCodes/70/70_A2025_NEC_P08_FD_PIResponses.pdf