General Requirements — ICC P1 Practice Questions

17 questions · 14% of the ICC P1 exam

Worked questions

1. Under 2024 IRC Section P2903.3.2, what is the maximum static water pressure for the domestic water supply system?

  • 80 psi
  • B60 psi
  • C70 psi
  • D50 psi

Where to look it up

https://codes.iccsafe.org/content/IRC2024V2.1/chapter-29-water-supply-and-distribution

Why A is correct

The static pressure may not exceed 80 psi. If the main pressure exceeds 80 psi, the section requires an approved pressure-reducing valve conforming to ASSE 1003 or CSA B356 on the domestic branch main or riser at its service connection. A main pressure of exactly 80 psi does not create the original invented requirement to reduce fixture pressure to 60 psi under this section. This is a static-pressure limit, not a fixture’s minimum pressure while flowing. Source: 2024 IRC, https://codes.iccsafe.org/content/IRC2024V2.1/chapter-29-water-supply-and-distribution

2. A remodel design specifies flexible, nonmetallic tubing for concealed hot- and cold-potable-water distribution inside an interior wall. Which proposed material meets that specification and the material-standard requirements of 2024 IRC P2906.5? Assume support, joint and protection requirements are met.

  • ACopper tubing complying with ASTM B88
  • BPVC pressure pipe complying only with the water-service standards of Table P2906.4
  • PEX tubing complying with ASTM F876 and NSF 61, rated at least 100 psi at 180°F
  • DGalvanized steel pipe complying with ASTM A53

Where to look it up

https://dos.ny.gov/nys-residential-code-noa-7242025

Why C is correct

The specified PEX tubing meets the nonmetallic tubing design and the cited distribution-pipe requirements. Copper and galvanized steel are metallic; PVC appearing in the water-service table is not thereby listed for this hot-and-cold interior distribution application. Concealment alone does not make PEX universally best or prohibit all other approved materials. Source: 2024 IRC P2906.5 and Table P2906.5, reproduced without a substantive state modifier in the official 2025 RCNYS (2024 IRC base). https://dos.ny.gov/nys-residential-code-noa-7242025

3. Under 2024 IRC P3005.3, what is the minimum uniform slope for a horizontal drainage pipe with a diameter of 2 inches?

  • A3/4 inch per foot
  • B1/2 inch per foot
  • 1/4 inch per foot
  • D1 inch per foot

Where to look it up

https://codes.iccsafe.org/content/IRC2024P2/chapter-30-sanitary-drainage

Why C is correct

Use the diameter condition in P3005.3: a 2-inch pipe is in the 2½-inch-and-smaller group, requiring a minimum ¼ inch of fall per foot. Site elevation does not select this minimum. Source: 2024 IRC P3005.3, https://codes.iccsafe.org/content/IRC2024P2/chapter-30-sanitary-drainage

4. Under 2024 IRC P3005.3, what is the minimum uniform slope for a horizontal drainage pipe with a diameter of 3 inches?

  • 1/8 inch per foot
  • B1/4 inch per foot
  • C3/8 inch per foot
  • D1/2 inch per foot

Where to look it up

https://codes.iccsafe.org/content/IRC2024P2/chapter-30-sanitary-drainage

Why A is correct

P3005.3 places 3-inch and larger horizontal drainage piping in the group requiring at least ⅛ inch of fall per foot. Select the diameter group before calculating fall; crawl-space ground slope is not the criterion. Source: 2024 IRC P3005.3, https://codes.iccsafe.org/content/IRC2024P2/chapter-30-sanitary-drainage

5. A listed vented gas fireplace requires 36 inches of side clearance to an unprotected combustible wall. Its listing permits use of the clearance-reduction method in 2024 IRC G2409.2. A 3 1/2-inch-thick masonry wall protector without a ventilated airspace is installed, meeting all applicable table notes. What minimum side clearance to the combustible wall does Table G2409.2 permit for this protection?

  • A6 inches
  • B12 inches
  • C18 inches
  • 24 inches

Where to look it up

https://dos.ny.gov/nys-residential-code-noa-7242025

Why D is correct

Use the 36-inch unprotected-clearance group, the sides-and-rear column and the row for 3 1/2-inch masonry without a ventilated airspace. The permitted minimum is 24 inches. The measurement is to the combustible surface, not just to the protector. A different protector or listing condition can give a different result; 12 inches is not a universal fireplace side clearance. Source: 2024 IRC G2408.5, G2409.2 and Table G2409.2, row 1, reproduced without a substantive state modifier in the official 2025 RCNYS (2024 IRC base). https://dos.ny.gov/nys-residential-code-noa-7242025

Practice all 17 General Requirements questions