For a Carrier 59SC6A furnace, Table 2 lists the top clearance from combustible material as 1 inch. An unprotected combustible surface is 3/4 inch above the top of the furnace. What is the clearance finding under this listed requirement?
- AAccept because the rear clearance is zero
- BAccept because all sides have the same clearance
- The top clearance is short by 1/4 inch
- DThe top clearance is short by 3/4 inch
Where to look it up
https://www.shareddocs.com/hvac/docs/1009/Public/0A/59SC6A-01SI.pdf
Why C is correct
Compare the specified top clearance with the measured top clearance: 1 − 0.75 = 0.25 inch short. A clearance listed for another face does not replace the top requirement. Source: https://www.shareddocs.com/hvac/docs/1009/Public/0A/59SC6A-01SI.pdf