ca-tradeTrade Knowledge (General Building B)hard

You are designing footings for a structure on loose sand with a bearing capacity of 1,500 psf. The column load is 45,000 pounds. What is the minimum required footing area?

Correct Answer

B) 30 sq ft

Required area = Load ÷ Bearing capacity = 45,000 lbs ÷ 1,500 psf = 30 square feet minimum.

Answer Options
A
35 sq ft
B
30 sq ft
C
25 sq ft
D
40 sq ft

Why This Is the Correct Answer

Option B (30 sq ft) is correct because the required footing area is calculated by dividing the column load by the soil bearing capacity: 45,000 lbs ÷ 1,500 psf = 30 square feet. This is the minimum area needed to spread the load without exceeding the soil's allowable bearing pressure.

Why the Other Options Are Wrong

Option A: 35 sq ft

Option A (35 sq ft) is incorrect. While a larger footing is structurally safe, the question asks for the MINIMUM required area. Using 45,000 ÷ 1,500 = exactly 30 sq ft — 35 sq ft exceeds the minimum and represents over-design.

Option C: 25 sq ft

Option C (25 sq ft) is incorrect. A 25 sq ft footing would produce a bearing pressure of 45,000 ÷ 25 = 1,800 psf, which exceeds the allowable 1,500 psf bearing capacity of the loose sand. This would cause excessive settlement or footing failure.

Option D: 40 sq ft

Option D (40 sq ft) is incorrect for the same reason as Option A — it is larger than the minimum required. The minimum is exactly 30 sq ft; 40 sq ft is oversized and not the answer sought.

Memory Technique

Think of soil bearing capacity as a 'weight limit per square foot.' To find how many square feet you need, divide total load by the limit per foot: A = L ÷ BC. Visualize spreading 45,000 pounds evenly across tiles where each tile holds 1,500 pounds — you need exactly 30 tiles.

Was this explanation helpful?

More ca-trade Questions

A contractor is installing shear walls in a residence located in Seismic Design Category D. The engineer's plans call for 15/32-inch structural sheathing with 8d nails at 6 inches on center at panel edges. The contractor wants to substitute 7/16-inch OSB with the same nailing. Is this substitution acceptable?

You are reviewing plans for a mixed-use building where the ground floor will house a restaurant with commercial kitchen equipment. The architect has specified standard residential electrical requirements throughout. What Title 24 compliance issue should you identify?

According to CBC seismic provisions, what is the concept behind the 'strong column, weak beam' design philosophy?

A residence in California has 2,800 sq ft of conditioned space. The HVAC system efficiency is 16 SEER. What is the approximate Title 24 compliance margin compared to the minimum 14 SEER requirement?

You're constructing a foundation on liquefiable soils identified in a California coastal area. The geotechnical report recommends deep foundations. Which option is most commonly specified?

A contractor is installing a heat recovery ventilation (HRV) system to comply with Title 24. The system serves a 2,000 sq ft house with 3 bedrooms. What is the minimum required ventilation rate?

During construction of a basement in sandy soil conditions, you encounter groundwater at 4 feet below grade. The basement extends 8 feet below grade. What is the critical design consideration per CBC?

During a seismic retrofit project, you discover that existing concrete has a compressive strength of 2,200 psi. The engineer specifies new anchor bolts that require 2,500 psi minimum concrete strength. What is the most appropriate action?

What is the maximum allowable notch depth in a 2x10 floor joist per CBC requirements?

You're reviewing plans for a wood-framed structure in seismic design category D. The project calls for a shear wall with 15/32-inch structural sheathing and 8d nails spaced 6 inches on center at panel edges. What is the allowable shear value per the CBC?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your Florida General Contractor exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.