EstatePass
ca-tradeTrade Knowledge (General Building B)hard

What is the fundamental period formula used in CBC for estimating the seismic period of a wood frame building?

Correct Answer

B) Ta = Ct × hn^x where Ct = 0.028

For wood frame buildings, CBC uses Ta = 0.028 × hn^0.8, where Ct = 0.028 for light frame wood construction and hn is the height in feet above the base.

Answer Options
A
Ta = Ct × hn^x where Ct = 0.035
B
Ta = Ct × hn^x where Ct = 0.028
C
Ta = Ct × hn^x where Ct = 0.020
D
Ta = Ct × hn^x where Ct = 0.030

Why This Is the Correct Answer

For wood frame buildings, CBC uses Ta = 0.028 × hn^0.8, where Ct = 0.028 for light frame wood construction and hn is the height in feet above the base.

Was this explanation helpful?

More ca-trade Questions

A contractor is installing shear walls in a residence located in Seismic Design Category D. The engineer's plans call for 15/32-inch structural sheathing with 8d nails at 6 inches on center at panel edges. The contractor wants to substitute 7/16-inch OSB with the same nailing. Is this substitution acceptable?

You are reviewing plans for a mixed-use building where the ground floor will house a restaurant with commercial kitchen equipment. The architect has specified standard residential electrical requirements throughout. What Title 24 compliance issue should you identify?

According to CBC seismic provisions, what is the concept behind the 'strong column, weak beam' design philosophy?

A residence in California has 2,800 sq ft of conditioned space. The HVAC system efficiency is 16 SEER. What is the approximate Title 24 compliance margin compared to the minimum 14 SEER requirement?

You're constructing a foundation on liquefiable soils identified in a California coastal area. The geotechnical report recommends deep foundations. Which option is most commonly specified?

A contractor is installing a heat recovery ventilation (HRV) system to comply with Title 24. The system serves a 2,000 sq ft house with 3 bedrooms. What is the minimum required ventilation rate?

During construction of a basement in sandy soil conditions, you encounter groundwater at 4 feet below grade. The basement extends 8 feet below grade. What is the critical design consideration per CBC?

During a seismic retrofit project, you discover that existing concrete has a compressive strength of 2,200 psi. The engineer specifies new anchor bolts that require 2,500 psi minimum concrete strength. What is the most appropriate action?

What is the maximum allowable notch depth in a 2x10 floor joist per CBC requirements?

You're reviewing plans for a wood-framed structure in seismic design category D. The project calls for a shear wall with 15/32-inch structural sheathing and 8d nails spaced 6 inches on center at panel edges. What is the allowable shear value per the CBC?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your Florida General Contractor exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.