In California wood frame construction, what is the required nailing pattern for 15/32-inch structural sheathing to wall studs?
Correct Answer
C) 8d nails at 6 inches on center at edges, 12 inches on center in the field
CRC Table R602.3(1) specifies that 15/32-inch structural sheathing must be attached to wall studs with 8d common nails spaced 6 inches on center along panel edges and 12 inches on center in the field. This nailing schedule provides adequate shear resistance for California's seismic requirements.
Why This Is the Correct Answer
CRC Table R602.3(1) specifies that 15/32-inch structural sheathing must be attached to wall studs with 8d common nails spaced 6 inches on center along panel edges and 12 inches on center in the field. This nailing schedule provides adequate shear resistance for California's seismic requirements.
More trade-general-building Questions
When installing engineered lumber joists (I-joists) in California residential construction, what is the primary code requirement for web stiffeners?
What is the required attic ventilation ratio when a vapor retarder is installed on the warm-in-winter side of the ceiling according to the California Residential Code?
In California's Wildland-Urban Interface (WUI) areas, which underlayment requirement applies to Class A fire-rated roof assemblies?
In California, when installing a tankless water heater in a seismic zone, what additional requirement must be met beyond standard installation practices?
According to the California Building Code (CBC), what is the minimum lap splice length for #4 rebar in a concrete foundation wall in normal weight concrete with f'c = 3000 psi?
According to CBC requirements for retaining walls in California, what additional design consideration must be addressed for retaining walls over 4 feet in height located in seismic design categories D, E, and F?
When constructing retaining walls in California that exceed 4 feet in height, which CBC requirement must be met regarding drainage?
Under California regulations, when is a reduced pressure principle (RPP) backflow prevention assembly required for a residential water service connection?
Under California Title 24, what is the minimum electrical service size required for new single-family residential construction?
According to the California Building Code, buildings located in Seismic Design Category D must comply with which specific seismic design requirements?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
In California seismic design, a building site with Vs30 = 250 m/s and located in an area with SMS = 1.8g would be classified as which Site Class according to CBC Chapter 16?
Next Question
When installing a solar photovoltaic system on a dwelling in California, what is the minimum required fire setback from the ridge of the roof according to California Fire Code requirements?