According to California Building Code Chapter 15, what is the minimum roof slope required for clay and concrete tile roofing?
Correct Answer
A) 2.5:12 (21% slope)
CBC Section 1507.3.3 requires clay and concrete tile roofing to have a minimum slope of 2.5:12 (21%). This is specific to California's adoption of the International Building Code with state amendments for tile roofing common in California's climate.
Why This Is the Correct Answer
CBC Section 1507.3.3 requires a minimum slope of 2.5:12 (approximately 21%) for clay and concrete tile roofing. Below this slope, water can back up under tiles and into the underlayment. California's code specifically adopts this threshold as a state amendment to the IBC given the prevalence of tile roofing in California climates.
Why the Other Options Are Wrong
Option B: 6:12 (50% slope)
6:12 is a much steeper threshold, sometimes associated with certain slate or wood shake requirements. Requiring 6:12 as a minimum for tile would eliminate most residential tile applications in California, which are commonly installed in the 3:12 to 5:12 range β well below 6:12.
Option C: 3:12 (25% slope)
3:12 is a plausible but incorrect answer. While tile can be installed at 3:12 with proper underlayment, the code-specified minimum is actually 2.5:12 β a slightly lower threshold. Selecting 3:12 would cause a contractor to decline installations that the code actually permits.
Option D: 4:12 (33% slope)
4:12 is above the minimum requirement and represents a more conservative slope than the code mandates. Installing tile at 2.5:12 is code-compliant; telling a client their 2.5:12 or 3:12 roof needs to be 4:12 before tile can be installed would be incorrect.
Memory Technique
Two-and-a-half bricks stacked = 2.5:12 slope. Visualize two and a half bricks leaning against a wall β that slight angle is just enough for water to run off tile before pooling. The '2.5' is the key number to lock in.
More trade-general-building Questions
When installing engineered lumber joists (I-joists) in California residential construction, what is the primary code requirement for web stiffeners?
What is the required attic ventilation ratio when a vapor retarder is installed on the warm-in-winter side of the ceiling according to the California Residential Code?
In California's Wildland-Urban Interface (WUI) areas, which underlayment requirement applies to Class A fire-rated roof assemblies?
In California, when installing a tankless water heater in a seismic zone, what additional requirement must be met beyond standard installation practices?
According to the California Building Code (CBC), what is the minimum lap splice length for #4 rebar in a concrete foundation wall in normal weight concrete with f'c = 3000 psi?
According to CBC requirements for retaining walls in California, what additional design consideration must be addressed for retaining walls over 4 feet in height located in seismic design categories D, E, and F?
When constructing retaining walls in California that exceed 4 feet in height, which CBC requirement must be met regarding drainage?
Under California regulations, when is a reduced pressure principle (RPP) backflow prevention assembly required for a residential water service connection?
Under California Title 24, what is the minimum electrical service size required for new single-family residential construction?
According to the California Building Code, buildings located in Seismic Design Category D must comply with which specific seismic design requirements?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
Under CALGreen (California Green Building Standards Code), what is the minimum required water efficiency for lavatory faucets in nonresidential buildings?
Next Question
For California Title 24 compliance, what is the maximum thermal bridging factor allowed for wood frame wall construction when calculating building envelope performance?