A grounding-type receptacle is replacing a device on an ungrounded circuit and no grounding path is available. Which approach may be permitted when correctly implemented?

California C-10 exam practice question · Finish Wiring & Trim

A grounding-type receptacle is replacing a device on an ungrounded circuit and no grounding path is available. Which approach may be permitted when correctly implemented?

  • AInstall a three-prong receptacle with no protection or label
  • Use a permitted labeled GFCI replacement method
  • CBond the grounding terminal to neutral at the receptacle
  • DConnect the grounding terminal to a water faucet

Why B is correct

The applicable GFCI replacement method can improve shock protection but does not create an equipment-grounding conductor and requires labeling. Neutral-ground bonding at the receptacle is improper.