What is the minimum concrete cover required for #6 rebar in a concrete footing that will be in direct contact with earth?
Correct Answer
C) 3 inches
According to ACI 318, reinforcing steel in concrete cast against and permanently exposed to earth requires a minimum cover of 3 inches. This protects the rebar from corrosion and ensures proper bond with the concrete.
Why This Is the Correct Answer
ACI 318 Building Code Requirements for Structural Concrete specifically requires 3 inches of concrete cover for reinforcing steel in concrete that is cast against and permanently exposed to earth. This requirement ensures adequate protection of the rebar from moisture, soil chemicals, and other corrosive elements that could compromise the structural integrity. The 3-inch cover also provides sufficient concrete thickness to develop proper bond between the rebar and concrete while maintaining the steel's structural capacity over the building's design life.
Why the Other Options Are Wrong
Option A: 1.5 inches
1.5 inches is insufficient cover for earth-contact applications and would only be appropriate for interior concrete members not exposed to weather or earth contact, where corrosion risk is minimal.
Option B: 2 inches
2 inches of cover is typically required for concrete exposed to weather or outdoor air, but not sufficient for direct earth contact where additional protection from soil moisture and chemicals is needed.
Option D: 4 inches
4 inches exceeds the minimum requirement and would be unnecessarily conservative, though not technically wrong - it's just not the minimum required by code.
Memory Technique
Think 'Dirt = 3' - when concrete touches dirt/earth, you need 3 inches of cover to protect the rebar from the harsh underground environment.
Reference Hint
ACI 318 Building Code Requirements for Structural Concrete, Chapter 20 - Concrete Cover Requirements, Table 20.6.1.3.1
More Project Mgmt Questions
What is the minimum R-value required for wall insulation in Florida Climate Zone 2?
A subcontractor brings a new chemical product to your jobsite. Under the Globally Harmonized System (GHS), what information must be immediately available to workers?
A construction site has a trench that is 8 feet deep in Type B soil. What is the maximum allowable slope ratio for the trench walls without protective systems?
A detail drawing shows a scale of 3/4" = 1'-0". If a dimension measures 2.25 inches on the drawing, what is the actual dimension?
What is the maximum recommended spacing between drywall screws when attaching to wood studs?
People Also Study
Business & Financial Management
120 questions · 70% to pass
Contract Administration
60 questions · 70% to pass
Previous Question
A chemical product's Safety Data Sheet indicates it has the GHS pictogram showing a flame over a circle. What type of hazard does this represent?
Next Question
You are excavating a trench that is 8 feet deep in Type C soil. What is the minimum required slope ratio for the sides of this excavation?