What is the maximum spacing for anchor bolts connecting wood sill plates to concrete foundations in Seismic Design Category D per the California Building Code?
Correct Answer
C) 6 feet on center
CBC Section 2308.3.1 specifies that anchor bolts must be spaced not more than 6 feet on center in Seismic Design Categories D, E, and F, with bolts required within 12 inches of each end of sill plates. This closer spacing compared to lower seismic zones ensures proper load transfer.
Why This Is the Correct Answer
CBC Section 2308.3.1 mandates anchor bolts spaced no more than 6 feet on center in Seismic Design Categories D, E, and F. This tighter spacing (compared to the 8-foot maximum allowed in lower seismic categories) ensures adequate shear force transfer between the wood framing and the concrete foundation during an earthquake.
Why the Other Options Are Wrong
Option A: 8 feet on center
8 feet on center is the maximum spacing permitted in lower seismic design categories (A, B, C). In SDC D, E, and F β which covers most of California β this spacing is too wide and does not meet the more stringent seismic requirements.
Option B: 10 feet on center
10 feet on center is not a recognized standard in the CBC for anchor bolt spacing. It exceeds even the less stringent 8-foot rule and would provide dangerously inadequate seismic connections in any California jurisdiction.
Option D: 4 feet on center
4 feet on center is more restrictive than required. While it would technically be safe, it is not the code maximum and represents unnecessary material and labor cost. The exam tests knowledge of the maximum allowed spacing, not the most conservative option.
Memory Technique
Associate 'D for Danger zone = 6 feet.' California is almost entirely in SDC D or higher, so for the California exam, default to 6 feet. Remember: '6 for seismic D, 8 for lower risk.'
More trade-general-building Questions
When installing engineered lumber joists (I-joists) in California residential construction, what is the primary code requirement for web stiffeners?
What is the required attic ventilation ratio when a vapor retarder is installed on the warm-in-winter side of the ceiling according to the California Residential Code?
In California's Wildland-Urban Interface (WUI) areas, which underlayment requirement applies to Class A fire-rated roof assemblies?
In California, when installing a tankless water heater in a seismic zone, what additional requirement must be met beyond standard installation practices?
According to the California Building Code (CBC), what is the minimum lap splice length for #4 rebar in a concrete foundation wall in normal weight concrete with f'c = 3000 psi?
According to CBC requirements for retaining walls in California, what additional design consideration must be addressed for retaining walls over 4 feet in height located in seismic design categories D, E, and F?
When constructing retaining walls in California that exceed 4 feet in height, which CBC requirement must be met regarding drainage?
Under California regulations, when is a reduced pressure principle (RPP) backflow prevention assembly required for a residential water service connection?
Under California Title 24, what is the minimum electrical service size required for new single-family residential construction?
According to the California Building Code, buildings located in Seismic Design Category D must comply with which specific seismic design requirements?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
For a new residential construction project in California, when is a reduced pressure principle (RPP) backflow prevention assembly required according to the California Residential Code?
Next Question
For special moment frame steel construction in California's highest seismic zones, which welding inspection requirement applies?