According to California regulations, what is the minimum concrete strength required for foundations in residential construction?
Correct Answer
A) 2,500 psi
CBC Section 1905.3.1 and California Residential Code Section R402.2 specify a minimum concrete compressive strength of 2,500 psi for foundation concrete in residential construction. This strength requirement ensures adequate durability and structural performance for foundations in California's varied soil and seismic conditions.
Why This Is the Correct Answer
CBC Section 1905.3.1 and California Residential Code Section R402.2 specify a minimum concrete compressive strength of 2,500 psi for foundation concrete in residential construction. This strength requirement ensures adequate durability and structural performance for foundations in California's varied soil and seismic conditions.
More trade-general-building Questions
When installing engineered lumber joists (I-joists) in California residential construction, what is the primary code requirement for web stiffeners?
What is the required attic ventilation ratio when a vapor retarder is installed on the warm-in-winter side of the ceiling according to the California Residential Code?
In California's Wildland-Urban Interface (WUI) areas, which underlayment requirement applies to Class A fire-rated roof assemblies?
In California, when installing a tankless water heater in a seismic zone, what additional requirement must be met beyond standard installation practices?
According to the California Building Code (CBC), what is the minimum lap splice length for #4 rebar in a concrete foundation wall in normal weight concrete with f'c = 3000 psi?
According to CBC requirements for retaining walls in California, what additional design consideration must be addressed for retaining walls over 4 feet in height located in seismic design categories D, E, and F?
When constructing retaining walls in California that exceed 4 feet in height, which CBC requirement must be met regarding drainage?
Under California regulations, when is a reduced pressure principle (RPP) backflow prevention assembly required for a residential water service connection?
Under California Title 24, what is the minimum electrical service size required for new single-family residential construction?
According to the California Building Code, buildings located in Seismic Design Category D must comply with which specific seismic design requirements?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
Under California's Title 24 Energy Code, which lighting control requirement applies to residential buildings with ceiling-mounted luminaires in rooms larger than 70 square feet?
Next Question
Under California's Title 24 Energy Code, what is the maximum allowable fenestration area as a percentage of conditioned floor area for residential buildings in Climate Zone 1?
